This will have to be built inside a water proof box, with a radiator/other provisions for dealing with heat.
All valves are line power – 110V or 3 phase, the pump is three phase
There will have to be manual override switches, usually with an “Off/On/Auto” feature, for all functions. We can send you our current box, with a Unitronics M 90 in it, if needed, but we think it would be better if you start from scratch.
The thermocouple inside the pasteurizer uses thermostatic wire, and is a:
Pyromation Thermosensor Model:KP43G09M/2 T163
Pyromation, Ft. Wayne, IN.
Pyromation.com
Reads 2˚ high at 51˚. May have an issue, or it may be in the Unitronics. Will need to be able to calibrate the thermocouple to read correctly.
“A” cycle
1. Open Hot Valves
2. Start Glycol Pump
3. Heat to X˚ F
a. If it does not change rapidly in temperature
i. Sound alarm
ii. Open all valves (this is to clear any air pockets which may have formed)
iii. Close all valves, except hot
4. Hold for Y minutes at X˚ F
5. Stop Glycol Pump
6. Close hot valves
7. Open City Water Tap
8. Open city water valves
9. Start Glycol Pump
10. Chill to 100˚F
a. If it does not change rapidly in temperature
b. Sound alarm
c. Open all valves for 1 minute
d. Close all valves, except city water
11. Stop Glycol Pump
12. Close City water valves
13. Close City Water Tap
14. Open Ice Builder valves
a. Possibly, start a circulator pump for the ice builder. Uncertain, will obtain more info from the manufacturer.
15. Chill to 36˚F
a. If it does not change rapidly in temperature
b. Sound Alarm
c. Open all valves for 1 minute
d. Close all valves, except ice builder
16. Stop glycol pump
17. Close ice builder valves
18. If temp rises to 38˚F
a. Open Ice builder valves
b. Start Glycol Pump
c. If it doesn’t work.
i. Stop glycol pump
ii. Close ice builder valves
iii. Start chiller
iv. Open chiller valves
v. Start glycol pump
“B” cycle
1. Open Hot Valves
2. Start Glycol Pump
3. Heat to P˚ F
a. If it does not change rapidly in temperature
i. Sound alarm
ii. Open all valves (this is to clear any air pockets which may have formed)
iii. Close all valves, except hot
4. Hold for Q minutes at P˚ F
5. Stop Glycol Pump
6. Close hot valves
7. Open city water valves
8. Start Glycol Pump
9. Chill to 100˚F
a. If it does not change rapidly in temperature
b. Sound alarm
c. Open all valves for 1 minute
d. Close all valves, except city water
10. Stop Glycol Pump
11. Close City water valves
12. Open Ice Builder valves
13. Chill to 36˚F
a. If it does not change rapidly in temperature
b. Sound Alarm
c. Open all valves for 1 minute
d. Close all valves, except ice builder
14. Stop glycol pump
15. Close ice builder valves
16. If temp rises to 38˚F
a. Open Ice builder valves
b. Start Glycol Pump
c. If it doesn’t work.
i. Stop glycol pump
ii. Close ice builder valves
iii. Start chiller
iv. Open chiller valves
v. Start glycol pump
“Caustic” Cycle
1. Open Hot Valves
2. Start Glycol Pump
3. Heat to 170˚ F
a. If it does not change rapidly in temperature
i. Sound alarm
ii. Open all valves (this is to clear any air pockets which may have formed)
iii. Close all valves, except hot
4. Stop Glycol Pump
5. Close hot valves
“Acid” Cycle
1. Open Hot Valves
2. Start Glycol Pump
3. Heat to 150˚ F
a. If it does not change rapidly in temperature
i. Sound alarm
ii. Open all valves (this is to clear any air pockets which may have formed)
iii. Close all valves, except hot
4. Stop Glycol Pump
5. Close hot valves
“Sanitizer” Cycle
1. Open Hot Valves
2. Start Glycol Pump
3. Heat to 140˚ F
a. If it does not change rapidly in temperature
i. Sound alarm
ii. Open all valves (this is to clear any air pockets which may have formed)
iii. Close all valves, except hot
4. Stop Glycol Pump
5. Close hot valves